I came across this on Pro Sound Web and feel it is very important for anyone working on older homes. People with bands and such that a simple set of testers will help to prevent injury or damage to gear.
Re: freak accident? help!
« Reply #18 on: May 03, 2012, 05:00:44 pm »
ReplyReply
ReplyQuote
Guys... this is not a freak accident. It was caused by something I call a Reverse Polarity Bootleg Ground (or RPBG). This occurs when an old building has new grounded outlets added by bonding the ground screw to the neutral screw because there was no separate ground wire to begin with. That by itself is electrically safe (however, it's illegal per the NEC), but many older buildings had black power wires for both the hot and neutral, and some were simply wired backwards with the white/neutral wire being hot and the black/power line being actual neutral. See the attached diagram. In that case any piece of gear plugged into a Reverse Polarity Bootleg Grounded outlet will have its chassis energized to 120 volts. If you then connect that piece of audio gear to something else that's plugged into a correctly wired outlet, you can have 20 amps or more of current flow down the shield, which melts wires and destroys gear. The really scary thing is that a 3-light tester will tell you that this reversed outlet is wired correctly, when in fact both the neutral and ground contacts are at 120 volts and the hot side is at earth potential. Please see http://www.youtube.com/watch?v=_pwCY4_L ... redirect=1 for a video I did a few weeks ago that describes how you can use a $20 non-contact AC tester in conjunction with a cheap 3-light tester to qualify grounds in power plugs. That's the only easy way to determine if an outlet will blow up your gear.
After discussing this testing issue with a few meter manufacturers, it seems that the entire industry has missed this problem. In fact, electrical inspectors routinely use a 3-light tester to qualify outlets in renovated buildings, but that's where the hot and neutral wires in the wall are most likely to be reversed.
I'm covering a lot of this on http://www.noshockzone.org and trying to get Lowes and Home Depot to offer training to consumers and electricians on how to check for this condition. Please contact me with any questions or comments.
Mike Sokol - mike@fitsandstarts.com
* Bootleg Ground Demo.JPG (83.56 kB, 776x565 - viewed 835 times.)
« Last Edit: May 19, 2012, 01:36:07 pm by Mike Sokol »
Report to moderator Logged
Mike Sokol
mike@fitsandstarts.com
Re: freak accident? help!
« Reply #18 on: May 03, 2012, 05:00:44 pm »
ReplyReply
ReplyQuote
Guys... this is not a freak accident. It was caused by something I call a Reverse Polarity Bootleg Ground (or RPBG). This occurs when an old building has new grounded outlets added by bonding the ground screw to the neutral screw because there was no separate ground wire to begin with. That by itself is electrically safe (however, it's illegal per the NEC), but many older buildings had black power wires for both the hot and neutral, and some were simply wired backwards with the white/neutral wire being hot and the black/power line being actual neutral. See the attached diagram. In that case any piece of gear plugged into a Reverse Polarity Bootleg Grounded outlet will have its chassis energized to 120 volts. If you then connect that piece of audio gear to something else that's plugged into a correctly wired outlet, you can have 20 amps or more of current flow down the shield, which melts wires and destroys gear. The really scary thing is that a 3-light tester will tell you that this reversed outlet is wired correctly, when in fact both the neutral and ground contacts are at 120 volts and the hot side is at earth potential. Please see http://www.youtube.com/watch?v=_pwCY4_L ... redirect=1 for a video I did a few weeks ago that describes how you can use a $20 non-contact AC tester in conjunction with a cheap 3-light tester to qualify grounds in power plugs. That's the only easy way to determine if an outlet will blow up your gear.
After discussing this testing issue with a few meter manufacturers, it seems that the entire industry has missed this problem. In fact, electrical inspectors routinely use a 3-light tester to qualify outlets in renovated buildings, but that's where the hot and neutral wires in the wall are most likely to be reversed.
I'm covering a lot of this on http://www.noshockzone.org and trying to get Lowes and Home Depot to offer training to consumers and electricians on how to check for this condition. Please contact me with any questions or comments.
Mike Sokol - mike@fitsandstarts.com
* Bootleg Ground Demo.JPG (83.56 kB, 776x565 - viewed 835 times.)
« Last Edit: May 19, 2012, 01:36:07 pm by Mike Sokol »
Report to moderator Logged
Mike Sokol
mike@fitsandstarts.com